    Any Sparkys? Electrical Question

    Got 2 new light fittings for the lounge - I've got them wired in and they work perfectly - wanted to check something.

    They are 2 cable fittings - so live/neutral but they are clear cased cables - one has text on the side of it - is this neutral or live?

    Would it not work properly if it was wired incorrectly - aka live on the light fitting to neutral on the lighting ring?

  2. #2
    Grumpy and VERY old :( g8ina's Avatar
    Join Date
    Nov 2006
    Location
    Northampton
    Posts
    6,623
    Thanks
    2,466
    Thanked
    1,556 times in 1,047 posts
    • g8ina's system
      • Motherboard:
      • ASRock Z75 Pro3
      • CPU:
      • Intel(R) Core(TM) i5-3570K CPU @ 3.40GHz 3.40 GHz
      • Memory:
      • 16GB Corsair 1600MHz DDR3.
      • Storage:
      • 250GB SSD system, 250GB SSD Data + 2TB data, + 8TB NAS
      • Graphics card(s):
      • XFX Radeon HD 6870
      • Case:
      • Coolermaster Elite 430
      • Operating System:
      • Win10
      • Monitor(s):
      • Iiyama 22"
      • Internet:
      • Virgin 100MB unlimited

    Re: Any Sparkys? Electrical Question

    Yes, it would go bang big time if you wired it wrong !

    If you can grab any of the text on the cable it would help ID it. Other than that I have no idea.
    Cheers, David



  3. #3
    DR
    DR is offline
    on ye old ship HEXUS DR's Avatar
    Join Date
    Jul 2003
    Location
    HEXUS HQ, Elstree
    Posts
    13,411
    Thanks
    1,058
    Thanked
    831 times in 372 posts

    Re: Any Sparkys? Electrical Question

    One strand has text the other doesn't - hence me thinking it's right...

    so it's 2 strand - I've wired one in to live, one in to neutral and it works fine...

  4. #4
    DR
    DR is offline
    on ye old ship HEXUS DR's Avatar
    Join Date
    Jul 2003
    Location
    HEXUS HQ, Elstree
    Posts
    13,411
    Thanks
    1,058
    Thanked
    831 times in 372 posts

    Re: Any Sparkys? Electrical Question

    So if you wired live to neutral and neutral to live it wouldn't work and would go pop?

  5. #5
    Does he need a reason? Funkstar's Avatar
    Join Date
    Aug 2005
    Location
    Aberdeen
    Posts
    19,874
    Thanks
    630
    Thanked
    965 times in 816 posts
    • Funkstar's system
      • Motherboard:
      • Gigabyte EG45M-DS2H
      • CPU:
      • Intel Core2Quad Q9550 (2.83GHz)
      • Memory:
      • 8GB OCZ PC2-6400C5 800MHz Quad Channel
      • Storage:
      • 650GB Western Digital Caviar Blue
      • Graphics card(s):
      • 512MB ATI Radeon HD4550
      • PSU:
      • Antec 350W 80+ Efficient PSU
      • Case:
      • Antec NSK1480 Slim Mini Desktop Case
      • Operating System:
      • Vista Ultimate 64bit
      • Monitor(s):
      • Dell 2407 + 2408 monitors
      • Internet:
      • Zen 8mb

    Re: Any Sparkys? Electrical Question

    It's AC, so getting live and neutral the wrong way round just means that a strand is peaking high when it should be peaking low. Makes no difference for a light and probably most other devices.

    DC is different. Applying a positive voltage to the end that is supposed to be grounded can be a very bad thing.

  6. #6
    DR
    DR is offline
    on ye old ship HEXUS DR's Avatar
    Join Date
    Jul 2003
    Location
    HEXUS HQ, Elstree
    Posts
    13,411
    Thanks
    1,058
    Thanked
    831 times in 372 posts

    Re: Any Sparkys? Electrical Question

    Quote Originally Posted by Funkstar View Post
    It's AC, so getting live and neutral the wrong way round just means that a strand is peaking high when it should be peaking low. Makes no difference for a light and probably most other devices.

    DC is different. Applying a positive voltage to the end that is supposed to be grounded can be a very bad thing.
    Yep pretty much what a friend who is a sparky has said to me - he just said becareful when changing the bulbs just incase well it's a glass surround so doesn't actually matter that much

    They kick ass.....got some of these bulbs in them: http://www.mimime.co/

  7. #7
    Seething Cauldron of Hatred TheAnimus's Avatar
    Join Date
    Aug 2005
    Posts
    17,164
    Thanks
    803
    Thanked
    2,152 times in 1,408 posts

    Re: Any Sparkys? Electrical Question

    Well it might fail and you'll be liable when changing a bulb, as your friend probably mentioned.

    Its not a case of a 'strand peaking high when it should be low' sorry but that's an odd way of thinking of it.

    AC voltage can be thought of as a hot, and a return. Don't touch the hot is a top tip.

    Normally with lighting you put the switch in the hot (or live, or phase, or whatever you want to call it) so that when you are changing a bulb the only circuit which isn't broken (switched off) is the return. The return is nothing more than a efficient path to the ground, so is less likely to harm. If you've got your light the wrong way round, rather than the hot been switched off, only the return will have been switched off, so guess what that means if you touch it whilst changing the bulb? The hot will have to return, via you, and you may well have a very bad time.

    If you have a tester, it will be worth using it to make sure you've got it the right way round! If you don't they are dirt cheap:
    http://www.amazon.co.uk/Black-Spur-S...6002011&sr=8-1
    Not even a quid. I always have one of these to make sure that the double check I've done has been sufficent. But then I've been in hospital thanks to an electrocution (which irritatingly wasn't my fault....)
    throw new ArgumentException (String, String, Exception)

  8. Received thanks from:

    DR (06-05-2012)

  9. #8
    Account closed at user request
    Join Date
    Aug 2003
    Location
    Elephant watch camp
    Posts
    2,150
    Thanks
    56
    Thanked
    115 times in 103 posts
    • wasabi's system
      • Motherboard:
      • MSI B85M-G43
      • CPU:
      • i3-4130
      • Memory:
      • 8 gig DDR3 Crucial Rendition 1333 - cheap!
      • Storage:
      • 128 gig Agility 3, 240GB Corsair Force 3
      • Graphics card(s):
      • Zotac GTX 750Ti
      • PSU:
      • Silver Power SP-S460FL
      • Case:
      • Lian Li T60 testbanch
      • Operating System:
      • Win7 64bit
      • Monitor(s):
      • First F301GD Live
      • Internet:
      • Virgin cable 100 meg

    Re: Any Sparkys? Electrical Question

    Personally I'd tape each end of the cable with red on whichever strand I'd have decided is live. Leccy tape is only a quid or so in any DIY shop. Will massively help when someone comes to extend the circuit later or make changes.

  10. #9
    Grumpy and VERY old :( g8ina's Avatar
    Join Date
    Nov 2006
    Location
    Northampton
    Posts
    6,623
    Thanks
    2,466
    Thanked
    1,556 times in 1,047 posts
    • g8ina's system
      • Motherboard:
      • ASRock Z75 Pro3
      • CPU:
      • Intel(R) Core(TM) i5-3570K CPU @ 3.40GHz 3.40 GHz
      • Memory:
      • 16GB Corsair 1600MHz DDR3.
      • Storage:
      • 250GB SSD system, 250GB SSD Data + 2TB data, + 8TB NAS
      • Graphics card(s):
      • XFX Radeon HD 6870
      • Case:
      • Coolermaster Elite 430
      • Operating System:
      • Win10
      • Monitor(s):
      • Iiyama 22"
      • Internet:
      • Virgin 100MB unlimited

    Re: Any Sparkys? Electrical Question

    My concern would have been if you had say, 2 light switches in the room, you have to sort of daisy chain to the second switch, and that's where you have the possibility of getting it the wrong way round and the fuses going pop. If its a single fitting to a single switch, then I don't see a problem.
    Cheers, David



  11. #10
    Seething Cauldron of Hatred TheAnimus's Avatar
    Join Date
    Aug 2005
    Posts
    17,164
    Thanks
    803
    Thanked
    2,152 times in 1,408 posts

    Re: Any Sparkys? Electrical Question

    Quote Originally Posted by g8ina View Post
    If its a single fitting to a single switch, then I don't see a problem.
    If you've not wired the switch yourself, yup.

    If you have wired the switch yourself make sure you switch the live.
    throw new ArgumentException (String, String, Exception)

  12. #11
    The late but legendary peterb - Onward and Upward peterb's Avatar
    Join Date
    Aug 2005
    Location
    Looking down & checking on swearing
    Posts
    19,378
    Thanks
    2,892
    Thanked
    3,403 times in 2,693 posts

    Re: Any Sparkys? Electrical Question

    For a two wire fitting, polarity is irrelevant to the operation of it. From a safety perspective, line should be switched anyway so no part of the fitting is live when the lamp is switched off. (Neutral should be at or near earth potential anyway)

    From a safety PoV, if the fitting is bayonet, it doesn't matter which way round it is wired. If it is edison screw, then the screw part should be connected to neutral, the centre contact to line.

    All exposed metal parts should normally be earthed. I'm guessing that as these fittings don't have UK colour coded cable, they are imports, in which case they may not meet UK safety standards. That doesn't mean that they are intrinsically dangerous, just that you have to be a little more careful in ensuring that they are connected safely. This is particularly true if it was designed for the US market operating at 115V, where the insulation standards may be less rigorous.

    To summarise TheAnimus's post, UK mains supply is not 'floating'. One side, neutral, is connected to earth at the distribution point (substation or distribution transformer) and at the supply side of the consumer unit (and often at many points in between). Line is at (nominally) 230 volts above earth potential, and that is the one that will bite if you touch it - which is why that should be switched, and connections/contacts protected.
    (\__/)
    (='.'=)
    (")_(")

    Been helped or just 'Like' a post? Use the Thanks button!
    My broadband speed - 750 Meganibbles/minute

  13. Received thanks from:

    DR (06-05-2012)

Thread Information

Users Browsing this Thread

There are currently 1 users browsing this thread. (0 members and 1 guests)

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •