    I'm not quite sure where to ask this so I'll try here as it may get a wider audience ?.

    Currently at work we've got an electrician on-site for a couple of month doing various bits and one of his tasks is to PAT test everything (I did this acouple of times in the 90's and hated, ****ty job !). Now, being that they're not hard wired to the mains a server is classed as a portable appliance, but I'll be honest and say that I don't want any PAT tester no matter how expensive it is doing earth tests or anything like that on ANY of my servers (e.g an HP DL380 G5 running ESX 3.5 and plenty of VM's).

    I've had a look at a few sites and there's nothing specific about what you can get away with as a 'visual' inspection. I'm going to fight tooth and nail for all UPS's + switches + servers to just be visualy inspected.

    Has anyone esle here been in a similar situation ?.

    ta
    I'm not fat and I'm not 40

    Quote Originally Posted by JPreston View Post
    I'm pretty disappointed that in the 21st century so much human endeavour and industry is still devoted to ascertaining whose imaginary sky-fairy is best...

  2. #2
    Comfortably Numb directhex's Avatar
    Join Date
    Jul 2003
    Location
    /dev/urandom
    Posts
    17,074
    Thanks
    228
    Thanked
    1,027 times in 678 posts
    • directhex's system
      • Motherboard:
      • Asus ROG Strix B550-I Gaming
      • CPU:
      • Ryzen 5900x
      • Memory:
      • 64GB G.Skill Trident Z RGB
      • Storage:
      • 2TB Seagate Firecuda 520
      • Graphics card(s):
      • EVGA GeForce RTX 3080 XC3 Ultra
      • PSU:
      • EVGA SuperNOVA 850W G3
      • Case:
      • NZXT H210i
      • Operating System:
      • Ubuntu 20.04, Windows 10
      • Monitor(s):
      • LG 34GN850
      • Internet:
      • FIOS

    Re: PAT testing servers (in computer room/data center situations)

    I'd like to meet the guy with a 32A commando connector on his PAT test gear

  3. #3
    DILLIGAF GoNz0's Avatar
    Join Date
    Jun 2006
    Location
    Derby
    Posts
    10,872
    Thanks
    632
    Thanked
    1,192 times in 945 posts
    • GoNz0's system
      • Motherboard:
      • Asus Rampage V Extreme
      • CPU:
      • i7 something X99 based
      • Memory:
      • 16gb GSkill
      • Storage:
      • 4 SSD's + WD Red
      • Graphics card(s):
      • GTX980 Strix WC
      • PSU:
      • Enermax Galaxy 1250 (9 years and counting)
      • Case:
      • Corsair 900D
      • Operating System:
      • win10 64bit
      • Monitor(s):
      • Dell 24"
      • Internet:
      • 220mb Cable

    Re: PAT testing servers (in computer room/data center situations)

    you quite simply tell him that they only need soft testing, a visual is also required. unless of course he signs the bit of paper accepting responsibility for any damage caused, he wont and will then do a soft test.

    i work on behalf of HP and they will not cover anything thats blown up after its been pat tested in the normal way, they will however cover soft testing as this doesnt damage the equipment,

    if he doesnt have the equipment to soft test, escort him off site.

    Tests on computer equipment are "soft tests" of 200mA on earth continuity. No operational tests are carried out on computer CPUs.

  4. #4
    Senior Member
    Join Date
    May 2006
    Location
    Wigan,Lancashire
    Posts
    401
    Thanks
    10
    Thanked
    16 times in 12 posts

    Re: PAT testing servers (in computer room/data center situations)

    I am probably way off the mark here but...

    I thought pat testing involved testing the lead to the appliance? Therefore this wouldnt affect your servers would it? Except they would have to be powered down?

  5. #5
    Senior Member Stringent's Avatar
    Join Date
    Jul 2003
    Location
    Neverland
    Posts
    5,227
    Thanks
    45
    Thanked
    155 times in 117 posts
    • Stringent's system
      • Motherboard:
      • Intel DQ57TM
      • CPU:
      • Intel i5 760
      • Memory:
      • 8GB
      • Storage:
      • 1TB
      • Graphics card(s):
      • NVIDIA Geforce 260GTX
      • PSU:
      • Corsair HX620
      • Case:
      • Coolermaster Centurion
      • Operating System:
      • Microsoft Windows 7 Ultimate x64
      • Monitor(s):
      • Dual Iiyama 24"
      • Internet:
      • Patchy

    Re: PAT testing servers (in computer room/data center situations)

    We have to have our servers PAT tested. They can be visually checked once, but next year they have to stick them on the meters. Usually there is no problem, but the guys who do our school stuff have decent machines to do it. They even print the labels off too!

  6. #6
    Senior Member
    Join Date
    Feb 2005
    Location
    Hampshire
    Posts
    571
    Thanks
    21
    Thanked
    11 times in 10 posts
    • Fatboy40's system
      • Motherboard:
      • Asus A8N-E
      • CPU:
      • A64 X2 4200+ @ 2420 MHz
      • Memory:
      • 2GB
      • Storage:
      • 200GB SATA
      • Graphics card(s):
      • PNY 8800 GTS 320 - 648 ROP/1512 Shader/1053 Mem
      • PSU:
      • 400w Enermax
      • Operating System:
      • Windows 7 Pro x86
      • Monitor(s):
      • 17" Acer Flat Screen

    Re: PAT testing servers (in computer room/data center situations)

    Quote Originally Posted by directhex View Post
    I'd like to meet the guy with a 32A commando connector on his PAT test gear
    You'll have to pay our shop floor a visit then, we've had to invest in this sort of kit to fully test some of the equipement there

    As long as the power cable's not permanently connected to the mains the equipment is portable, even if it take a fork lift to move it
    I'm not fat and I'm not 40

    Quote Originally Posted by JPreston View Post
    I'm pretty disappointed that in the 21st century so much human endeavour and industry is still devoted to ascertaining whose imaginary sky-fairy is best...

  7. #7
    Senior Member
    Join Date
    Feb 2005
    Location
    Hampshire
    Posts
    571
    Thanks
    21
    Thanked
    11 times in 10 posts
    • Fatboy40's system
      • Motherboard:
      • Asus A8N-E
      • CPU:
      • A64 X2 4200+ @ 2420 MHz
      • Memory:
      • 2GB
      • Storage:
      • 200GB SATA
      • Graphics card(s):
      • PNY 8800 GTS 320 - 648 ROP/1512 Shader/1053 Mem
      • PSU:
      • 400w Enermax
      • Operating System:
      • Windows 7 Pro x86
      • Monitor(s):
      • 17" Acer Flat Screen

    Re: PAT testing servers (in computer room/data center situations)

    Thanks for that GoNz0

    Quote Originally Posted by GoNz0 View Post
    i work on behalf of HP and they will not cover anything thats blown up after its been pat tested in the normal way, they will however cover soft testing as this doesnt damage the equipment
    I'm very interested in this, is there any way of obtaining proof of this policy or is this just info for HP internal consumption ?.
    I'm not fat and I'm not 40

    Quote Originally Posted by JPreston View Post
    I'm pretty disappointed that in the 21st century so much human endeavour and industry is still devoted to ascertaining whose imaginary sky-fairy is best...

  8. #8
    Senior Member
    Join Date
    Feb 2005
    Location
    Hampshire
    Posts
    571
    Thanks
    21
    Thanked
    11 times in 10 posts
    • Fatboy40's system
      • Motherboard:
      • Asus A8N-E
      • CPU:
      • A64 X2 4200+ @ 2420 MHz
      • Memory:
      • 2GB
      • Storage:
      • 200GB SATA
      • Graphics card(s):
      • PNY 8800 GTS 320 - 648 ROP/1512 Shader/1053 Mem
      • PSU:
      • 400w Enermax
      • Operating System:
      • Windows 7 Pro x86
      • Monitor(s):
      • 17" Acer Flat Screen

    Re: PAT testing servers (in computer room/data center situations)

    Quote Originally Posted by Stringent View Post
    ...but the guys who do our school stuff have decent machines to do it. They even print the labels off too!
    Same here, but from what I know/understand there's allways the possibility that you can end up with a fried piece of hardware.

    All you need is someone to use the wrong test, or for there to be something slightly wrong with the hardware being tested. I'd rather have a server with a fault that MAY last me until it gets replaced (or before then it may be replaced anyhow due to increased load/usage) than a server killed off by someone trying to do there job.
    I'm not fat and I'm not 40

    Quote Originally Posted by JPreston View Post
    I'm pretty disappointed that in the 21st century so much human endeavour and industry is still devoted to ascertaining whose imaginary sky-fairy is best...

  9. #9
    Senior Member
    Join Date
    Feb 2005
    Location
    Hampshire
    Posts
    571
    Thanks
    21
    Thanked
    11 times in 10 posts
    • Fatboy40's system
      • Motherboard:
      • Asus A8N-E
      • CPU:
      • A64 X2 4200+ @ 2420 MHz
      • Memory:
      • 2GB
      • Storage:
      • 200GB SATA
      • Graphics card(s):
      • PNY 8800 GTS 320 - 648 ROP/1512 Shader/1053 Mem
      • PSU:
      • 400w Enermax
      • Operating System:
      • Windows 7 Pro x86
      • Monitor(s):
      • 17" Acer Flat Screen

    Re: PAT testing servers (in computer room/data center situations)

    Quote Originally Posted by shackahn View Post
    I thought pat testing involved testing the lead to the appliance?...
    That's just one part of it, there can be much more e.g. if the applicance has exposed metal there's earth tests to be done etc.
    I'm not fat and I'm not 40

    Quote Originally Posted by JPreston View Post
    I'm pretty disappointed that in the 21st century so much human endeavour and industry is still devoted to ascertaining whose imaginary sky-fairy is best...

  10. #10
    DILLIGAF GoNz0's Avatar
    Join Date
    Jun 2006
    Location
    Derby
    Posts
    10,872
    Thanks
    632
    Thanked
    1,192 times in 945 posts
    • GoNz0's system
      • Motherboard:
      • Asus Rampage V Extreme
      • CPU:
      • i7 something X99 based
      • Memory:
      • 16gb GSkill
      • Storage:
      • 4 SSD's + WD Red
      • Graphics card(s):
      • GTX980 Strix WC
      • PSU:
      • Enermax Galaxy 1250 (9 years and counting)
      • Case:
      • Corsair 900D
      • Operating System:
      • win10 64bit
      • Monitor(s):
      • Dell 24"
      • Internet:
      • 220mb Cable

    Re: PAT testing servers (in computer room/data center situations)

    its in the regs m8, not an internal thing just following the guidelines, computer equipment is not to be pat tested the normaly way as you will blow something up nearly every time, the regs point out that they should be soft tested to confirm the earth is working with no more than 200ma..

    i raised the question to hp's tech line after a customer admitted the pc that had a dead psu, ram and cpu had just been pat tested as it had a failed sticker on it, i spoke to the company who tested it and they said they had pat tested in the normal way, i told hp and got a call back explaining the regs and that the units warranty was now null and void due to the full pat test.

    i took great pleasure informing the customer who also took great pleasure in ringing the sparky and informing him he was liable as he didnt do the correct test and owed themover £1000, he refused to pay, the customer then pointed out that they had not payed the fee for testing all the equipment and if he wanted the balance he should pop round..

    if you need proof have a google around, i found this on the 1st hit http://www.electratest.com/testing.htm

    see section 4

    also

    http://www.pat-testing.info/PAT-Testers.htm

  11. #11
    Senior Member
    Join Date
    Feb 2005
    Location
    Hampshire
    Posts
    571
    Thanks
    21
    Thanked
    11 times in 10 posts
    • Fatboy40's system
      • Motherboard:
      • Asus A8N-E
      • CPU:
      • A64 X2 4200+ @ 2420 MHz
      • Memory:
      • 2GB
      • Storage:
      • 200GB SATA
      • Graphics card(s):
      • PNY 8800 GTS 320 - 648 ROP/1512 Shader/1053 Mem
      • PSU:
      • 400w Enermax
      • Operating System:
      • Windows 7 Pro x86
      • Monitor(s):
      • 17" Acer Flat Screen

    Re: PAT testing servers (in computer room/data center situations)

    This is the tester being used...

    http://www.pat-testing.info/seaward-europaplus.htm

    ... and it has an 'IT Earth Continuity Test' which is about all I'm going to allow on the servers, but can it be successfully tested whilst a server is running and connected the mains/a ups ?.
    I'm not fat and I'm not 40

    Quote Originally Posted by JPreston View Post
    I'm pretty disappointed that in the 21st century so much human endeavour and industry is still devoted to ascertaining whose imaginary sky-fairy is best...

  12. #12
    DILLIGAF GoNz0's Avatar
    Join Date
    Jun 2006
    Location
    Derby
    Posts
    10,872
    Thanks
    632
    Thanked
    1,192 times in 945 posts
    • GoNz0's system
      • Motherboard:
      • Asus Rampage V Extreme
      • CPU:
      • i7 something X99 based
      • Memory:
      • 16gb GSkill
      • Storage:
      • 4 SSD's + WD Red
      • Graphics card(s):
      • GTX980 Strix WC
      • PSU:
      • Enermax Galaxy 1250 (9 years and counting)
      • Case:
      • Corsair 900D
      • Operating System:
      • win10 64bit
      • Monitor(s):
      • Dell 24"
      • Internet:
      • 220mb Cable

    Re: PAT testing servers (in computer room/data center situations)

    no u will need to power down each server and unplug from the ups, best bets a late night/weekend call

  13. #13
    Senior Member Stringent's Avatar
    Join Date
    Jul 2003
    Location
    Neverland
    Posts
    5,227
    Thanks
    45
    Thanked
    155 times in 117 posts
    • Stringent's system
      • Motherboard:
      • Intel DQ57TM
      • CPU:
      • Intel i5 760
      • Memory:
      • 8GB
      • Storage:
      • 1TB
      • Graphics card(s):
      • NVIDIA Geforce 260GTX
      • PSU:
      • Corsair HX620
      • Case:
      • Coolermaster Centurion
      • Operating System:
      • Microsoft Windows 7 Ultimate x64
      • Monitor(s):
      • Dual Iiyama 24"
      • Internet:
      • Patchy

    Re: PAT testing servers (in computer room/data center situations)

    If something does blow up as a result, think of it as a nice shiny new server.

  14. #14
    Senior Member
    Join Date
    Feb 2007
    Location
    Leicester
    Posts
    221
    Thanks
    2
    Thanked
    3 times in 3 posts

    Re: PAT testing servers (in computer room/data center situations)

    Hmm. I'm sure we were told by our safety office that these days computer equipment does not need to be PAT tested. It's generally only things that tend to get moved around alot - kettles, fans etc. Will check with one of the guys who does our testing.
    _ _ _
    Vroomy

  15. #15
    Senior Member
    Join Date
    Feb 2007
    Location
    Leicester
    Posts
    221
    Thanks
    2
    Thanked
    3 times in 3 posts

    Re: PAT testing servers (in computer room/data center situations)

    here you go:
    http://www.hse.gov.uk/pubns/indg236.pdf

    Page 7 - suggested Inital Intervals

    IT; eg desktop computers, VDU screens:
    User checks - No
    Formal visual inspection - every 2-4 years
    Combined inpection and testing - No if double insulated - otherwise 5 years

    So if they are less than 5 years old tell them to stuff their testing kit where the sun don't shine and do a visual inspection. Pages 4-5 tell you what to lok out for in a visual inspection - no need to unplug them from my interpretation.
    _ _ _
    Vroomy

  16. #16
    Boooooom Barakka's Avatar
    Join Date
    Jul 2003
    Location
    ...fixing it in post
    Posts
    1,361
    Thanks
    61
    Thanked
    127 times in 104 posts

    Re: PAT testing servers (in computer room/data center situations)

    Yep, it's all a matter of interpretation, servers in a comms room, fair enough, if the recommendation is not for the first 5 years then fine, leave it til then. If it's a PC in a high traffic environment like a warehouse then i'd recommend every 12-18 months. But don't forget after this initial test it would be onto the default 12-18 months interval.

    But you will need to have a formal visual inspection, and yes, it should be unplugged because the visual inspection should be checking the full length of the mains lead, the pins and casing of the plug, and the rating of the fuse in the plug, if it's done properly.

    Also, anyone who's had any PAT training in the last 5 years should know you only test IT equipment with mA loads.
    Quote Originally Posted by The Mock Turtle
    “Reeling and Writhing, of course, to begin with, and then the different branches of arithmetic -- Ambition, Distraction, Uglification, and Derision."
    System:Atari 2600 CPU:8-bit 6507 (1.19MHz) RAM:128 bytes Colours: 16 (4 on screen) Resolution: 192x160

Page 1 of 2 12 LastLast

Thread Information

Users Browsing this Thread

There are currently 1 users browsing this thread. (0 members and 1 guests)

Similar Threads

  1. Replies: 22
    Last Post: 03-09-2008, 04:45 PM
  2. Replies: 0
    Last Post: 17-04-2007, 09:43 AM
  3. ATI Catalyst 5.8 released
    By =TcQi= in forum Graphics Cards
    Replies: 17
    Last Post: 18-08-2005, 12:35 AM
  4. Soak Testing new computer
    By bettercomputers in forum PC Hardware and Components
    Replies: 7
    Last Post: 22-08-2003, 10:10 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •