    Re: UPS for section of my network

    How does this look?

    Computer hardware and software at amazing prices, available online from Scan Computers UK

    Its about 40% over what we need so has a bit of head way for anyexpansion I can in this rack. I can't see much more going in this rack its already holding ......

    2 x Dell 1600SC
    1 x DL380 G5
    2 x DL320
    1 x Cisco 2950XL
    1 x LCD monitor
    1 x Compaq KVM
    1 x NAS
    and a Compaq 1000Mb fiber hub
    □ΞVΞ□

  2. #18
    Senior Member burble's Avatar
    Join Date
    May 2007
    Location
    Olney
    Posts
    1,138
    Thanks
    8
    Thanked
    90 times in 89 posts

    Re: UPS for section of my network

    If it'll give you enough runtime then go for it. Again though, it doesn't have a network management card built in.

  3. #19
    The late but legendary peterb - Onward and Upward peterb's Avatar
    Join Date
    Aug 2005
    Location
    Looking down & checking on swearing
    Posts
    19,378
    Thanks
    2,892
    Thanked
    3,403 times in 2,693 posts

    Re: UPS for section of my network

    If you need the network management card (which allows you to monitor it remotely) then this is the one.

    Computer hardware and software at amazing prices, available online from Scan Computers UK

    If you are using it to hold up two computers, then the UPC needs to send a shutdown signal to both and the network management card may do that too, but I haven't researched this - it is left as an exercise for the reader Or I can do it for your company on a consultancy basis
    (\__/)
    (='.'=)
    (")_(")

    Been helped or just 'Like' a post? Use the Thanks button!
    My broadband speed - 750 Meganibbles/minute

  4. Received thanks from:

    Jay (18-01-2008)

  5. #20
    Senior Member burble's Avatar
    Join Date
    May 2007
    Location
    Olney
    Posts
    1,138
    Thanks
    8
    Thanked
    90 times in 89 posts

    Re: UPS for section of my network

    Quote Originally Posted by peterb View Post
    If you are using it to hold up two computers, then the UPC needs to send a shutdown signal to both and the network management card may do that too, but I haven't researched this)
    It does

    Don't do what a colleague did though and plug the management card into a switch that wasn't UPS powered. The power went, as did the switch so the servers didn't get the signal to shutdown. Whoops.

  6. #21
    The late but legendary peterb - Onward and Upward peterb's Avatar
    Join Date
    Aug 2005
    Location
    Looking down & checking on swearing
    Posts
    19,378
    Thanks
    2,892
    Thanked
    3,403 times in 2,693 posts

    Re: UPS for section of my network

    Quote Originally Posted by burble View Post
    It does

    Don't do what a colleague did though and plug the management card into a switch that wasn't UPS powered. The power went, as did the switch so the servers didn't get the signal to shutdown. Whoops.
    Bet he only did it the once though!!
    (\__/)
    (='.'=)
    (")_(")

    Been helped or just 'Like' a post? Use the Thanks button!
    My broadband speed - 750 Meganibbles/minute

  7. #22
    Jay
    Jay is offline
    Gentlemen.. we're history Jay's Avatar
    Join Date
    Aug 2006
    Location
    Jita
    Posts
    8,365
    Thanks
    304
    Thanked
    568 times in 409 posts

    Re: UPS for section of my network

    I did that once as well. £3,500 of damage!! Only did that once.

    Will add that to the list. Thanks.

    If you don'twant to have to buy the card you can use the method here

    What APC powerchute version will shutdown multiple computers? : apc, powerchute, computers, shutdown

    I do that at home but I don't trust it for business.
    □ΞVΞ□

  8. #23
    Senior Member burble's Avatar
    Join Date
    May 2007
    Location
    Olney
    Posts
    1,138
    Thanks
    8
    Thanked
    90 times in 89 posts

    Re: UPS for section of my network

    Quote Originally Posted by peterb View Post
    Bet he only did it the once though!!
    Oh yes, he won't be making that mistake again.

  9. #24
    Registered+
    Join Date
    Jan 2008
    Posts
    27
    Thanks
    0
    Thanked
    0 times in 0 posts
    • adam_weisshaupt's system
      • Motherboard:
      • MSI K8 Diamond Plus
      • CPU:
      • AMD Opteron 170
      • Memory:
      • Corsair TWINXP2048-3200C2
      • Storage:
      • 2TB spread over 7 HDDs
      • Graphics card(s):
      • ATI Radeon X1800
      • PSU:
      • 620W Enermax Liberty
      • Case:
      • Akasa Eclipse
      • Monitor(s):
      • simple 19" Hyundai
      • Internet:
      • 4Mbps cable

    Re: UPS for section of my network

    Is the APC SMARTUPS you are thinking about ordering a ONLINE UPS or just LINE INTERACTIVE? Had a look on their site but they don't say [or I couldn't find]. If it is an ONLINE UPS then it sounds good [especially for the price you found via amazon]. If it is a LINE INTERACTIVE UPS then I would not recommend it. A UPS is a crucial [yet mostly neglected] part of an installation and anything less than ONLINE double conversion technology only causes problems. Example: you can connect the whole world [exaggeration] to a LINE INTERACTIVE UPS and it will not tell you that it is overloaded [because it is basically a fancy mutliplug as long as its AC source provides it with power] until you have a power outage - then it will go into internal fault and die because all of a sudden it can only supply a load at its rated VA value. A ONLINE UPS is always supplying your load by its battery and will tell you if you overload it even if its AC source is ok.

  10. #25
    Jay
    Jay is offline
    Gentlemen.. we're history Jay's Avatar
    Join Date
    Aug 2006
    Location
    Jita
    Posts
    8,365
    Thanks
    304
    Thanked
    568 times in 409 posts

    Re: UPS for section of my network

    its Line Interactive but it does have overload warnings

    Any advice on adding this to an already populated rack? Always been the first thing I normally add and removing the hardware will take way to long and be a nightmare of a job.
    Last edited by Jay; 22-01-2008 at 01:31 AM.
    □ΞVΞ□

  11. #26
    Jay
    Jay is offline
    Gentlemen.. we're history Jay's Avatar
    Join Date
    Aug 2006
    Location
    Jita
    Posts
    8,365
    Thanks
    304
    Thanked
    568 times in 409 posts

    Re: UPS for section of my network

    I can see why I used to get other people to instll UPS devices.... heavy!!
    □ΞVΞ□

  12. #27
    The late but legendary peterb - Onward and Upward peterb's Avatar
    Join Date
    Aug 2005
    Location
    Looking down & checking on swearing
    Posts
    19,378
    Thanks
    2,892
    Thanked
    3,403 times in 2,693 posts

    Re: UPS for section of my network

    Quote Originally Posted by jay_oasis View Post
    I can see why I used to get other people to instll UPS devices.... heavy!!

    Yes! And of course (SOTBO) ideally it needs to go at the bottom of the rack! (particularly if the rack is free standing)
    (\__/)
    (='.'=)
    (")_(")

    Been helped or just 'Like' a post? Use the Thanks button!
    My broadband speed - 750 Meganibbles/minute

  13. #28
    Jay
    Jay is offline
    Gentlemen.. we're history Jay's Avatar
    Join Date
    Aug 2006
    Location
    Jita
    Posts
    8,365
    Thanks
    304
    Thanked
    568 times in 409 posts

    Re: UPS for section of my network

    yes, the rack is clear at the bottom with the UPS rails already in place. (Its a 42U Compaq 9000 Series rack)

    Just going to be very hard for 2 of us to put it in... don't want to topple the rack!
    □ΞVΞ□

  14. #29
    The late but legendary peterb - Onward and Upward peterb's Avatar
    Join Date
    Aug 2005
    Location
    Looking down & checking on swearing
    Posts
    19,378
    Thanks
    2,892
    Thanked
    3,403 times in 2,693 posts

    Re: UPS for section of my network

    can you install it without the batteries, then replace them when the chassis is in place?
    (\__/)
    (='.'=)
    (")_(")

    Been helped or just 'Like' a post? Use the Thanks button!
    My broadband speed - 750 Meganibbles/minute

  15. #30
    Jay
    Jay is offline
    Gentlemen.. we're history Jay's Avatar
    Join Date
    Aug 2006
    Location
    Jita
    Posts
    8,365
    Thanks
    304
    Thanked
    568 times in 409 posts

    Re: UPS for section of my network

    yes, the batteries just slide out but its still heavy. Should be ok though.

    Just going to get started... wish me luck.
    □ΞVΞ□

  16. #31
    Jay
    Jay is offline
    Gentlemen.. we're history Jay's Avatar
    Join Date
    Aug 2006
    Location
    Jita
    Posts
    8,365
    Thanks
    304
    Thanked
    568 times in 409 posts

    Re: UPS for section of my network

    Well we had a power failure on Monday night and the UPS held the systems up until the power came back on.
    □ΞVΞ□

Page 2 of 2 FirstFirst 12

Thread Information

Users Browsing this Thread

There are currently 1 users browsing this thread. (0 members and 1 guests)

Similar Threads

  1. Computer on network has lost connection to network
    By Furton in forum Networking and Broadband
    Replies: 9
    Last Post: 19-08-2011, 04:31 PM
  2. Network wont reconnect
    By htid in forum Networking and Broadband
    Replies: 1
    Last Post: 22-04-2006, 10:29 PM
  3. Small Home Network Setup Problems
    By ToxicPanda in forum Help! Quick Relief From Tech Headaches
    Replies: 2
    Last Post: 08-09-2004, 11:36 PM
  4. Network broken?
    By MAS in forum PC Hardware and Components
    Replies: 7
    Last Post: 01-10-2003, 02:02 AM
  5. Wired+Wireless home network purchasing recommendations...
    By D001 in forum Networking and Broadband
    Replies: 4
    Last Post: 01-09-2003, 11:03 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •